You can start with following points as reference:
6 i$ ?8 t9 A0 W2 |* P' F0 u. f+ y' o) a1 a
. Control a bus voltage more than once would lead to diverge. The PV bus is voltage controlled already, even though you has not designate the controlling generator.
, ~) v* r9 E) C% j# i' @6 ` . Control the high and low side voltage of a transformer would lead to diverge. The PV bus is voltage controlled already.
) G- M7 `6 G* S) K . Data input error could lead to diverge also. See post below.
/ W2 `. p, {7 d% ^0 L+ s4 t5 l$ s9 W+ Q( G) E6 a- q
楼主似乎是你的发电机数据填错了。因为你已经单独填写了四台发电机的升压变压器,所以在发电机数据里面就不要再写一遍了,即应该这么些0 r; }* R0 D4 K9 S* ^
1, '1', 700, 0, 288, -288, 1.03, 0, 100, 0, 1, 0, 0, 1, 1, 100.0, 900, 450, 1,1" n4 K3 R' d+ [0 h7 G) E, @4 a) C
2, '1', 700, 0, 288, -288, 1.01, 0, 100, 0, 1, 0, 0, 1, 1, 100.0, 900, 450, 1,1% k; N: m9 Q) K+ b7 x1 D
3, '1', 700, 0, 288, -288, 1.03, 0, 100, 0, 1, 0, 0, 1, 1, 100.0, 900, 450, 1,1
# ^* e4 h- l# i9 j+ \$ N 4, '1', 700, 0, 288, -288, 1.01, 0, 100, 0, 1, 0, 0, 1, 1, 100.0, 900, 450, 1,1# v- n7 \' z" G& B# _