发表于 2015-6-5 10:47:35
|
显示全部楼层
The impedances required in ETAP Transformer Editor are test data (or short-circuit
2 _% l$ h) b. ^9 i- vimpedances) given by manufacturer. They are NOT THE EQUIVALENT Delta-circuit
7 @! R8 y: ~/ u1 S' h, L5 Qimpedances of transformer. These values can be converted to the individual winding$ X' q5 f, J: j* h7 A5 S4 f
impedances or the equivalent Y-circuit impedances using the following formulas:
/ i; }7 x7 {4 _# OZp = 0.5 (Zps + Zpt – Zst)& d4 N8 X: J' N: [6 M
Zs = 0.5 (Zps + Zst – Zpt)
8 r0 ? d" L- FZt = 0.5 (Zpt + Zst – Zps), [3 |! {$ q) _4 k! Z. ^
To obtain the equivalent Delta-circuit impedances the Y to D-circuit transformation; G6 F' |2 z4 v9 B( n4 E9 \
formula is as follows:
" X3 l" n: x; m7 {5 s# i) SZPS = (ZpZs + ZpZt + ZsZt)/Zt
7 T# s- \; v$ a# I" hZPT = (ZpZs + ZpZt + ZsZt)/Zs7 e: B) V* ~# g: I
ZST = (ZpZs + ZpZt + ZsZt)/Zp |
评分
-