发表于 2015-6-5 10:47:35
|
显示全部楼层
The impedances required in ETAP Transformer Editor are test data (or short-circuit
, S5 a" j8 N6 X; \- e. J% n5 ~- @4 gimpedances) given by manufacturer. They are NOT THE EQUIVALENT Delta-circuit, E0 T. h& J/ y! O, v$ p
impedances of transformer. These values can be converted to the individual winding7 a; l: h! W& L% S2 Z; J
impedances or the equivalent Y-circuit impedances using the following formulas:
7 F( k9 O9 [9 |0 GZp = 0.5 (Zps + Zpt – Zst)
* f! }% Z' \1 s" A2 gZs = 0.5 (Zps + Zst – Zpt)
: L, V; D. [$ N, Y* RZt = 0.5 (Zpt + Zst – Zps)
2 F* C- J5 d% JTo obtain the equivalent Delta-circuit impedances the Y to D-circuit transformation) k1 g. x. b" U/ M' d$ Z
formula is as follows:
: T% m G! Y0 qZPS = (ZpZs + ZpZt + ZsZt)/Zt) q+ f4 a% A& j9 a& V& }3 n
ZPT = (ZpZs + ZpZt + ZsZt)/Zs
4 K d( Y1 [- i4 W) jZST = (ZpZs + ZpZt + ZsZt)/Zp |
评分
-
查看全部评分
|