The impedances required in ETAP Transformer Editor are test data (or short-circuit
" A) _1 y) C; K7 W# V4 v8 V) Uimpedances) given by manufacturer. They are NOT THE EQUIVALENT Delta-circuit& O7 `9 ?" ?5 I: x9 N5 k1 b! w
impedances of transformer. These values can be converted to the individual winding
% J" e, [2 M; N# ?# Zimpedances or the equivalent Y-circuit impedances using the following formulas:/ o) v" M, ]! m
Zp = 0.5 (Zps + Zpt – Zst)" C$ B9 W8 c+ }& f/ w3 ~, C6 N
Zs = 0.5 (Zps + Zst – Zpt)) z3 N( f5 q3 o6 A3 c: J8 q: v
Zt = 0.5 (Zpt + Zst – Zps)
: s- f8 a3 K" K& XTo obtain the equivalent Delta-circuit impedances the Y to D-circuit transformation8 F% p: P/ h9 n) i' Z0 d0 N
formula is as follows:
( p3 }0 D" \# {7 P$ g! f+ p# BZPS = (ZpZs + ZpZt + ZsZt)/Zt; l1 m( D3 @$ G! d
ZPT = (ZpZs + ZpZt + ZsZt)/Zs
! R) G- K4 \( \0 iZST = (ZpZs + ZpZt + ZsZt)/Zp |