On-Line Tap Changer# ^6 S: n% r" g) |( `1 F: ]
All transformer components are equipped with an on-line tap changer. When the tap changer is enabled, a diagonal line will appear on the component graphic, labelled Tap.
1 Q' F2 N7 _) d5 z5 \! TA change in tap setting is modeled as a change in the turns-ratio of the transformer. The per-unit leakage reactance and magnetizing currents, specified for 100% tap, are used to calculate admittances for the new voltage rating, corresponding to the tap setting. / E. ? {/ m7 A- {8 e1 [
EXAMPLE:# c+ N j. J9 }% B" K: R
Let us assume for simplicity, that a transformer is configured as Y-Y, with winding voltages rated at 10 kV primary and 100 kV secondary, and a tap changer is placed on the primary winding. The turns-ratio for this transformer is of course 1:10.
$ b! n# b; f( @) ?; [! Z( IAn on-line tap input of 1.0 corresponds to a 100% tap (i.e. no tap adjustment). If the tap input value is adjusted to say 1.05, then the turns-ratio would become 1.05:10 or 1:9.52381.
. J n' p5 z( F9 @7 uIt is possible to have a continuous change of tap, but this would require a re-ordering of the network solution every time step. It is more practical to change tap settings in steps, either through manual adjustment, using a slider or rotary switch, or from a controller with appropriate delays and steps built in. |
|